Hazen Williams C factor in HDPE pipe

Hello,

I am an engineering student doing a literature review on HW C-factor in HDPE pipe. In particular, I am looking for papers or studies relating to C-factor testing performed on HDPE pipe (ideally water main) that have been in service for a number of years. I have been having a hard time locating information on the age-related effects on HW C-factors in HDPE pipe.

If anyone knows of any information relating to HW C-factors for in service HDPE water main it would be very much appreciated.

Thank You!
Reply With Quote
  #2 (permalink)  
Old 12-07-2006, 03:09 PM
Registered User
 
Join Date: Dec 2006
Posts: 1
Re: Hazen Williams C factor in HDPE pipe

Use a Hazen Williams C Factor of:

150 for HDPE or PVC plastic pipe

The C value is the friction factor of the pipe material. The C value does not change based on length of pipe. This assumes you are using Hazen Williams equation for water or dirty water (sanitary sewers).

http://www.plasticpipe.org/pdf/pubs/...king_water.pdf
Reply With Quote
  #3 (permalink)  
Old 12-07-2006, 04:01 PM
Registered User
 
Join Date: Jan 2005
Posts: 2
Re: Hazen Williams C factor in HDPE pipe

Thank you for the reply.

I am more concerned with wether or not that C-factor of 150 will stay the same over the service length of the pipe.

Will the C-factor still be 150 after 35 plus years of service?

Or will it degrad to a lower value, and if so by what degree?

Is there anyone has gone back and done a C-factor test on a HDPE pipe that has been in service for a significant amount of time?
Reply With Quote
  #4 (permalink)  
Old 12-07-2006, 06:05 PM
Registered User
 
Join Date: Sep 2006
Posts: 2
Re: Hazen Williams C factor in HDPE pipe

This is a problem related with hydraulic networks calibration. There are a lot of problems carrying out the calibration processes. I have done that for a network composed by pipes of PVC and Asbestos Cement. I have not seen anything related with HDPE. I can tell you that my results conclude a high reduction of the C coefficient (Abestos cement from 135 to 80-85). But consider that in these results is included de uncertainty in the pressure and flow measurement.
Reply With Quote
  #5 (permalink)  
Old 01-19-2007, 10:33 PM
Registered User
 
Join Date: Jan 2007
Posts: 1
Re: Hazen Williams C factor in HDPE pipe

You are entering an interesting field. I see that after more than a month you have not really gotten answer to the specific question you asked (prompting you to ask it again). I am aware that in some of the earlier days of piping, unlined or various thin bituminous lined iron and steel pipes were in various fashion flow tested to see what head loss occurred in that (of course then most often relatively “new”) piping. I suspect some designers probably went out and designed more piping, assuming that was the flow performance they would have in the field. It was eventually found that over a period of time there was more pressure drop in (or less water delivery from) some of that piping than what there was initially. In the most prevalent cases where substantial changes were seen (when there were not other more obvious causes such as closed valves, obstructions, sediments, large leakages etc.), it was eventually found that the reductions in flow were either the result of scale build-up due to very hard waters, or instead internal tuberculation/corrosion build-up in pipes carrying certain soft and aggressive water conditions (see prior thread on this forum, before I joined, that discusses some aspects of this at http://www.bossintl.com/forums/showt...ight/hdpe.html). Both these conditions in their most severe forms in effect substantially reduce the internal flow diameter of pipe, of course with an understandable, substantial reduction in time in the “C-factor”.
With that industry knowledge and the subsequent development of cement mortar linings (first used e.g. in some USA iron pipes in 1922), I believe there was then greater sensitivity to flow properties and the subject of maintenance of flow properties over time. For this reason I know many utilities worked with first the Cast Iron Pipe Research Association (CIPRA) and then later the Ductile Iron Pipe Research Association (DIPRA) to run flow tests on sections of their piping, to get a better feel for what flow was actually being achieved by that piping in the field (with normal quality of installation and other real world effects etc.), and in some cases they repeated these tests over time to see what was happening in these areas of their systems. Voluminous results of this field research are of course now available as a result of this experience e.g. in Tables 1 and 2 of the publication at http://www.dipra.org/pdf/cementMortarLinings.pdf (I think more than sixty flow tests of working cement lined iron pipelines over a near 80 year time span, and at least in recent decades I believe virtually all accomplished by registered professional engineers and with no little interest of the utilities involved, are represented in these tables), as well as many other published studies by other third-parties. I would also recommend reading the passage, “Flow Coefficient…” on page 6 of this DIPRA document, as I believe it refers/has relevance to other types of pipes. I believe it is not unusual to see just a few points drop in any installed pipeline over many years, including even cement lined pipes that don’t significantly tuberculate (as illustrated in Table 2). This can occur in some cases for many reasons, including many that may have absolutely nothing to do with the condition of the contact surface of the pipe. However, you do not normally see drastic drop as in unlined pipes (unless there is a reason other than tuberculation). E.g. I believe any types of material pipelines can develop air locks and/or sedimentation, or formation of “scales” etc., if the flows and/or water chemistry etc. is such so as to result in such effects.
It seems quite odd however (considering the fact that they claim to have been around at least to some extent for many decades) that similar published databases are apparently not available for the plastics. I believe flow performance of installed pipelines is thus far more complicated than laboratory testing of a few pipes, and for that matter should be far more than perception bourne by plastic marketing hype (or even the “feel” of a pipe wall). In this regard (I think as also taught by the aforementioned earlier post on this forum) the flow performance of most at least contemporary types of pipe with effectively clean water laboratory flow performance only a few percent off the “smooth pipe curve”, including perhaps hdpe piping at least that is not too “wavy” and with the internal “beads” removed, is most likely best predicted by the actual internal flow diameter of the pipe (of course the outside diameter minus the sum of the wall thicknesses). I would be very careful otherwise about plugging in more favorable flow coefficients for even treated water piping that are not reasonably substantiated by field testing/experience.
I believe gravity sewer pipes and force mains (some subject to low or intermittent flows) can additionally be a special case, due to more likelihood of significant slimes, sedimentations, obstructions etc., that I believe incidentally can occur in any piping material.
ASCE MOP No. 60 (WPCF MOP No. FD-5), “Gravity Sanitary Sewer Design and Construction” suggests the same range of Mannings “n” values for “Cement-lined and seal coated cast iron” and “plastic pipe (smooth)” (both namely 0.011-0.015). The 1997 version of “Recommended Standards for Wastewater Facilities” (Ten States Standards) stated under Section 48.6 Design Friction Losses (sub-section 48.61 Friction Coefficient), “…for other smooth pipe materials such as pvc, polyethylene, lined ductile iron, etc. a higher “C” value not to exceed 120 may be allowed for design.”
While I realize the plastic pipe industry advertises/claims extremely favorable flow coefficients, you may be interested in the threads http://www.eng-tips.com/viewthread.c...=124331&page=9 , the site http://www.canclay.com/htdocs/Slimin...es%20Large.pdf , the thread at http://www.eng-tips.com/viewthread.c...73633&page=19, and the table “C-factor Values…” in the “C. Tables” section of the relatively new reference at http://www.haestad.com/library/books...tml/wwhelp.htm , that may give other glimpses of the real world. Sorry for the long post, but I noticed you were a student (who might have some interest in this history) and perhaps also this will prompt better response for you. Good luck with your project.

Randy Conner
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are Off
[IMG] code is Off
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


All times are GMT. The time now is 01:32 AM.